what is the method to measure the transformer current
carrieng capacity in three phase.
Answer Posted / deepakindi1
same as u do in for any 3 phase circuits
ie KW=sqrt(3)*V*I*cos(@)
WKT cos(@)=KW/KVA
SO KW/cos(@)=KVA
KVA=sqrt(3)*V*I
I=KVA/sqrt(3)*V
FOR EXAMPLE CONSIDER 11KV/440V 100KVA TRANSFORMER
AT PRIMARY
I=100/sqrt(3)*11
I=100/(1.732*11)
I=5.24A
AT SECONDARY I=100/sqrt(3)*.44
I=100/(1.732*.44)
I=131.24A
Is This Answer Correct ? | 7 Yes | 4 No |
Post New Answer View All Answers
Why collecting electrode of ESP to be earthed
Parts of machine and their discription in details with suitable photo
How to improve fuel cell in a distribution system?
What is the practical way to calculate the cable size for known ampere load?
In which working principal temperature transmitter work.explain in detailed.
What is the difference IN MCCB's between thermal magnetic and electronic tripping system ?
What are the types of feedback oscillators?
What is Icu and Ics and what is difference b/w them. please tell me how to calculate a size of a copper bar for a system or a breaker... reply on... king.arish@gmail.com would be waiting for a logical answer.
i have applied for the post of RRB section engineering chennai board please send me previou papers and solved answer. my mail id jagarapusrinivas@gmail.com
What is oscillator circuit?
what is the series parallel connection of capacitors? and how can we use these application in three phase motors for controlling torque?
in non technical way how can u define POWER FACTOR??
What are the ratings of VCB, MCB, MCCB, SF6, ACB, and OCB?
H.t motor 6600 volt to same motor lt supply 440volt supply applyed to h.t motor to effect....
What is the RME and explain the full form and what is the RME work?