Please tell me 1 ton = How many Kilowatt (Electrical)

Answer Posted / nitin jadhav

1 TR is equivalent to 907.185 US ton.
907.185 US Ton = 12000 BTU/hr
1 Btu/hr = 1055 joule
Now,
1 TR = 12000*1055/3600
= 3.51 KW

Is This Answer Correct ?    1 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

why three phase capacitor takes unbalanced current in capacitor bank?

1017


What happens to voltage when current is zero?

779


excitation limit of an excitor

1532


What's mean HVF & HAF in Vacuum Circuit Breaker?

4744


there is an alternator 480 k.w, 400v,50hz, 4-wire running on load having leakage alternator body earthed current 38 A. is it within acceptable limit? if yes then give reference if no then how to bring within specified limit

1496






I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?

1411


ELECTRICAL DRIVES: can a motor load system with passive load torque can have equilibrium speed in second quadrant

5655


can the measured percentage error during calibration of single phase energy meter be negative?

1929


why single CT used in DOL starter power circuit?

2068


How to check 11000/1.732 to 110/1.732 Potentila transformer (PT)?

1764


What is the effect of positive feedback on the stability of the systems?

650


what's the difference between abs/inc encoders. apart from the position remembrance what are all the other differences. and what's mean by grey code.

1577


whether starting current is limited to rated current of motor through soft starting or it exceeds the rated current?

1049


why the electrolyte level in lead acid battery is maintained 2.5 cms above electrodes?

1412


we have 15 ampere variyac but we want 30 ampere variyac what we do

1425