why capacitor bank shorted by resistance ( 3 terminal )
Answer Posted / m.r.vijayaraghavan
to self discharge before taking up maintenance work,otherwise you have to manually discharge the charge.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
What are the major reasons for balancing hydro-thermal mix?
What is a slack bus?
How to megger test 11 kV cable and the acceptance IR value
Give me the calculation steps to design an electromagnet to be work in 230V 50 Hz AC Supply. Also give force that is created by that electromagnet when it gets energized.
In between UPS out going changer over switch and ups raising main input, both side cable gland producing heat but the cable doesn't get heat,Why?
Which device is used for the source of emission of electrons in a crt?
How much weight an electrical engine can pull??
in the case of 6.6kv motor starter combination contain fuses on it VCB. but in 11KV motor starter combination Fuses are not using in it's VCB why?
excitation limit of an excitor
how dose servo motor works
The electromagnetic torque developed is proportional to what in a D.C series motor?
what is ramping rate of generator
What is the difference between Generator Differential Relay and Transformer Differential Relay?
to hook up ten 50 amp rv pedastels at a lenth of 600 feet from the service what size will my service need to be and the size of wire will I have to run to each pedastel in series??????
SIR, GIVE ME OPGW SAG CALCULATION FORMULA I AM DAE ELECTRICAL. THANKS