Differentiate between power relay and reverse power relay?
Answer Posted / deepak.vin208
Power Relay will operate when the power is more than the set irrespective of the direction where as reverse power relay will operate when the power is transferring the opposite direction...
Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
Explain The Application Of Storage Batteries?
What is the ratio of true power to apparent power in an ac circuit?
A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is observed the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?
how to interlock 3 nos MCCBs using under voltage coil. please provide me circuit diagram?
If I want to connect a capacitor bank on the HT side of a 11kV/415V, 3 phase delta-star distribution transformer to supply Reactive power to it..what practical specifications of a Capacitor bank that can i've??please reply..
hello! sir i did three year of diploma in electrical (2007- 2010) and now i m a student of electrical engineering. sir can i apply for germany visa for study and part tome work over there?
What are the various kind of cables used for transmission?
How to calculate that clean water supply in one Day from 150 KLD STP?
what kn of disc is used in 33kv,132kv,220kv,400kv,800kv transmission line
what happens if earth of 33kv cable is not connected to earthing pits? please send this query's answer to ngrm.sudha249@gmail.com
Difference between field rheostat and armature rheostat.
What willbe change in programming when we use 5/3 solenoid inplace of 5/2 in operating of a cylinder?
What do you understand by external characteristics of a d.c. Generator?
what is the difference between dry and wet type of 132kV terminations. which one is durable
if there are six generators (3 gas CATT, one Jenbacher o1 MW each, and two nos Diesel 01 no 01 mw other 0.65mw EDGs ( say), 3 CAtt gas set have identical pole pitch,01mw EDG and Jenbacher gas Set have different pole pitch, how their power connection can be done to connect a common bus bar during installation. in short, how different pole pitched generators power connection can be done to connect a common busbar system through generators incomer ACBs.