Answer Posted / banda saivarun
it is a Vector group of transformer
Vector group means it defines the primary & secondary side connection type. It says D for the delta connections (windings connected between two phases) & Y for the star connections (windings connected from each phase to ground). The 11 stands for the phase displacement of the secondary referenced to the primary. Imagine a clock with only an hour hand; at 11 o'clock, the hand is at 30 degrees to the reference (12 c'clock), so the secondary is at 30 degrees to the primary. tor group of transformer
| Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
what is relay what is protection & contact multiplying relays where it is used function in brief
Define availability (operational)?
Explain advantages of storage batteries
why do we use spark detector inside the slip ring brush compartment 0ona slip ring induction motor?
What would cause a 240v choke that should give 110v out on a 16w lamp to gradually increase to 160v?
What is the actual meaning of thermal power efficiency ?
WHY IN AC DRIVES,INPUT PHASE CURRENT SHOW UNBALANCE?
for 4 MVA , 33K.V/6.6K.V transformer. secondary side the connected load is 3000H.P. What is the rating of capacitor bank to be insttaled.
what percent do you derate your copper wire when you change from copper buss to copper wire
why T/F winding temp measurement cts are odd secondary current ie,109A/1.2A/1.4A?
What is the basic principle of operation of alternators/dc generators?
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
Define end float in a motor?
Is there any type of starter for DC motor other than two point,Three point and Four point starters?
what is differnce btwen lll and lllg faults