Answer Posted / gokul singh

VCB means vacuum circuit breaker it used in high voltage
(HV) lines
It has one mechanism in this mechanism spring is there it
is connected with small electric motor for charging the
spring but we can do manually charge also by this spring
tension circuit closing or circuit open can be done. The
circuit closing can be done by (CC closing coil) also.
In VCB CT are used for measuring, controlling & protection
purpose.

ACB means air circuit breaker it is used in low voltage
(LV) lines
It has also one mechanism it also work same.
ACB has (UV Under voltage) it used for tripping purpose
when power fail.
It has (CC Closing coil) for closing the circuit.
CT are used for measuring, controlling & protection purpose

Is This Answer Correct ?    12 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

write circuit diagram for a motor rotate in forward direction once it started and when pressed the same button it should rotate in anticlockwise.

2070


what is lumped and distributed elements?

1549


Please send 110 kv sb station full single line drawing(sld)

2060


how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec.

1739


Classify milling machines.

655






how we provide neutral earth on synchronising panel as per electrical standards?

1596


What is excitation in case of dc motor?

679


Explain the experiment on ward leonard method of a speed control on a dc shunt motor with an suitable circuit diagram.

2108


why EMF IS INDUCED IN A CONDUCTOR WHEN FLUX LINKING WITH IT CHANGES ACCORDING TO FARADAYS LAW.

1545


Cb closed condition if there is a tcs fail whether cb will trip or not

1321


what is invertor supply and raw powersupply

1532


at what rate the micro controller increment its timer....is it 1micro seconds or 1/(12*10^6) seconds

1350


difference between Ac and Dc mcb ????

1135


how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?

1406


where the lexical paramater will use in fron end?

1449