What is the main difference between power transformer and
Distribution transformer?
Answer Posted / pratikchattopahyay2
rating greater than 1 MVA treated as power transformer , rating less than 1 MVA treated as distribution transformer.
Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
at which voltage level arcing ground is occurs ??????????
armature winding of dc machine produce alternating emf then it convert in to dc by using commutator.But only we consider armature resistance why don't we consider inductive reactane effect?
Installation resistance for whole installation of 16 kva & 25 KVA DTRA a) Between each conductor b) between conductor to earth c) installation resistance for each apparatus, each conductor to earth d) earth resistance for the system of earthing
What is the significance of integral controller and derivative controller in a pid controller?
What is meant by full pitched winding?
What is error of a measurement?
Give some differences between open loop and closed loop?
Tell me about ur past electrical maintanence job
we have earthmat at 110KV substation.we would like to take earth resistance.b some says that by connecting earth megger terminals (C1,P1) at middile point of earthmat (at riser) will cause voltage gradient at other earthmat nods and dont get exat earth resistance.when connecting at end nods will get exat value . is it correct .please explain
what exactly commisioning work does in electrical site work... LT side?..
What are the basic properties of signal flow graph?
what are the preventive maintanance actions taken for air circuit breaker? please answer me
How to calibrate or test an LT Air Circuit breaker 440 volts, 35 KA, 800 Amps ?
Application Comparison between 22KV (UE)and 33KV (E) system. Are we allowed to use 33KV (E) cable in lieu of 22KV (UE) cable. What are the technical disadvantages.
WITCH CARDS IN USE IN FIRE CONTROL PANEL.