Answer Posted / carl_ellis
A seal pot has had two major uses:
a) a seal pot is intended to protect primary instruments
like pressure gauges, pressure or differential pressure
transmitters from the attack by the chemically agressive
medium being measured.
b) Seal pots have been used for differential pressure flow
measurement of low viscosity oils at high temperature where
cooling in the impulse tubing causes the liquid medium to
cool, become more viscous and to make the meter response
sluggish. By using a lighter, less viscous oil on the top
of the heavier, more viscous measured medium, all contained
in a seal pot that transmits the impulse tubing pressure to
the top of the seal pot, measurement response can be improved.
A test cock installed in a horizontal port tap is used to
establish the level of the heavier fluid (fill until it runs
out the cock) because the seal pot levels of the heavier
fluids must be at a known elevations in order to maintain
the transmitter's zero. A fill cock on the top of the seal
pot allows the light top fluid to be filled over the heavier
fluid.
High and low side sealing pots are generally connected very
close to the pipe.
The challenge is finding media that are compatible yet will
not mix and dilute one another.
Carl Ellis
Measure First
Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
Can anyone send most commonley asked Instrumentation questions and answers in cement industry please?
Specify for Cables - Flame Retardant and Fire Resistant?
how u calibrate sox nox co2 co in cemps?what is opacity n HPm?tell the standard parameters of cems?
why we are using drum level control valve air to close?
I installed the smartplant instrument v8, but can not be opened, that always said: "INTools 2007 hardlock no found". So Could you help me how to do for that?
what is the criteria to decide conductor size of a cable ?
How to Calibrate Ultrasonic flow Transmitter in Field
In a gas over oil actuator, after the opening/closing of valve, how the gas is vented out? How does the hydraulic/gas circuit function?
How is automatic reference junction compensation carried out in temperature recorders?
Specify ideal accuracy of flow element like orifice plate, Ventury, Annubar. Ultrasonic flow meter etc.
wich is coming the first HAZOP OR SIL
Can anybody tell me how to select the size of earthing cable for DCS & PLC system.Please tell me any relevant answer here or mail it to me.
how can i check vortex shedder bar it is ok? if there is ohms condition are shown correct?
explain key exchanges in all security modes WPA,WPA2,TLS?
What denotes the 5/8mm in the 3300XL 5/8mm proximitor probe?