Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

WHY EXCITATION OF SYNCHRONOUS MACHINE IS DC NOT AC

Answer Posted / anil

Yes we can have a ac in rotor.But then we will not call it as a rotor.It will be stationary but this rotor has to be connected to a 3phase supply .Then it will produce a rotating magnetic field which will interact with the stator and create emf.

Is This Answer Correct ?    0 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

May I know how much values to be set for earth fault, over current and short circuit values at 11kv side? I have 11kv van 1250amps rating. Present it's taking load 80amps?

1506


Give atleast 20 alternating current apparatus and devices.

1791


The loads are connected with phase and ground then why current flow as the loads ?

1985


if we run a 3 phase machine on two phase what will happend??? given answer with solid reason please

2104


What is the minimum distance to be maintained in between HT panel and LT panel and Instrument panel as per IEC and NEC standards?

1743


1- XC and the RC time constant are both measures of the reaction of C to a change in ____? 2-The power factor is a numerical ratio with a value between 0 and 1 equal to the ______________ of the phase angle. 3-When V and I are out of phase because of reactance, the product of V times I is called ______________ power 4-For _____________ inductors, the branch currents can be added algebraically. 5- The ______________ power in watts can be calculated as I^2R 6-Calculate XL with L = 30mH and f = 1kHz ( I have Xl=2piFL 2*3.141592653*1kHz*30mH =188 ohms Please check) 7-A parallel RL circuit has the values, R = 5kohms, XL = 5kohms. A voltage source of Vt = 10Vrms is connected in parallel to R and L. Determine the total current, It delivered by the voltage source Vt. 8-A series RC circuit has R = 1Mohm and C = 1microF. How long would it take for the capacitor to fully discharge if it is initially fully charged? 9-A circuit has real power = 300W and an apparent power of 500VA. Determine the power factor and phase angle. 10-The time constant for an LR series circuit is T = 0.1s and R = 10ohms. Calculate the inductance L.

3388


what is the efficiency of thyristor

1661


can any one suggest me the tilt angle of my solar pannel ?? or tell me how can i know the fix tilt angle of my solar pannel?? my cordinates are 31.503629,72.993164.

1819


what is the effect of earth on capacitance in 3-phase and 1- phase transmission line?

2376


Determine a suitable number of slors and conductors per slot for the starter 1 winding of a 3 phase, 3300 V. SO Hz 300 rpm alternator. The diameter is 2.3 m

2847


how to calculate the size of the HT cable

1905


I need the recommended size for a 3 phase transformer at 13.8 KV Primary and connected loads of 3000 kVA at 4200 volts and 2375 kVA @ 480 volts AC.

2043


If you have an earth with pilecap then your resistance is really low. why and how?

2025


why is using sensor?what is differece between photoelectric and proxmitty?

2019


Why 15Amp. MCB is suitable to carry load of 1.5Ton Ac please Explain?

2181