what is hot loop check and cold loop check.
Answer Posted / guest
A Cold Loop check is cold because it is done without
powering the loop.
A cold check consists of checking wire continuity from the
field instrument through junction boxes and through DCS/PLC
marshalling panel terminals to the control panel. Once
continuity has been confirmed, then a Hot Loop Check is
performed on the Loop's I/O.
A Hot loop check is 'hot' because it is done with the loop
powered up.
A Hot loop check consists of
- simulating a process input at the field instrument and
then checking the instrument's output and the response to
the process signal input at DCS/PLC.
- simulating outputs at the control end and checking for
correct response at the field end.
Carl Ellis
Measure First
Is This Answer Correct ? | 13 Yes | 1 No |
Post New Answer View All Answers
how to calibrate 0- 150 psi presure gauge by dead weght tester
flow transmeter accuracy 0.075% of full scale & find ucertainty is 0.025 % so what is maximum limit band of uncertainty
To become an Instrument DESIGN engineer, is there any softwares or training to become Instrument Design engineer, plz suggest me, Iam very much interested in designing.
i want to find out iffco get test paper
What is Predictive Maintenance
full process of gas turbin?
How to check vortex flow meter is in good condition while we do not having calibration setup?
How we can check the 2 wire proxy switch? & how it is connected to DI MODULE OF PLC?
What is the differerence between hysterisis and linearity.
What is the purpose of bypass valve across AS valve.
What is the reason PT speed not incresed in gas turbine?
why we should maintain neutral earth voltage below 1V while calibration? why cant it be 1.2V or 2V
How to find out the current of two motors having same power consumption but different RPM?
you must show the examples application and give at least 4 types of transducer/sensors that can minimize the failure during the manufacturing of the resistors.
How we calculate orifice plat size???