HOW TO MEASSURED THE AMPS RATING FOR SUITABLE CABLE SIZE?
Answer Posted / gaurav gupta
for al cable - 1 to 1.5 amp per sq.mm area
for cu cable - 2 to 2.5 amp per sq.mm area
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
What is the previous name of Cox's Bazar
What will be the current drawn by HT motor, if low voltage is applied.. any formula to calculate the LT amps of HT motor.?
in a solar power plant,we are going to step up the voltage 350V to 33kv, and to 132kv GSS. i want to ask that if it is possible that 315v/33kv is not possible because we also use 315v/11kv. or it should be 415v/33kv? is it effects generation or losses? the second question is-generation is depends on LV winding? or LV winding design for generation voltage?
what is the current setting for different relay protection for transformer .
what is the use of vcb & isolator in substation?
how we decide the require size is this for a known current at fuu load?
what is the formula for efficiency of francis turbine and generator for hydropower? what is best way to select francis turbine and generator?
How Can You Relate Power Engineering With Electrical Engineering?
Why collecting electrode of ESP to be earthed
why incomer bay is required before transformer bay if there are more than 1 nos. of transformer bay.
Can any one give an explanation about rating factors of cable? if we are laying the cable on the air with an temp 15 degree then rating factors will be 1.15 and if we are laying the cable on the air an temp 60 degree then rating factor will be 0.76 please describe it and what is the difference between rating factor and derating factor?
What is current & voltage ? Voltage perform at any load without current or not?
What is the alternate solution for testing of polarity by using polarity tester while its milli ammeter does not works?
what is the necessity of under ground cables ??
hey guys help me out.....what are the industrial uses/functions of nozzles in industries