If the neutral wire go pass through the core balance current
transformer? If yes then why? and no then why?
Answer Posted / kj
The neutral is requiered to pass through the core balance
CT together with the phase for the same circuit. It
operates on the current going through the pahse being
balanced with the current returning through the neutral. If
these are balanced the protection will not operate. If a
fault occurs (a short circuit to earth in either the phase
or neutral)some current will flow through the earth to the
neutral and not go through the CBCT. This will then operate
the protection.
Is This Answer Correct ? | 6 Yes | 1 No |
Post New Answer View All Answers
what is the meaning of WYE and DELTA in Electric meter?
if i get a drop in my 1st year and the i clear my 2nd year and 3rd year all clear and i dont have any back logs so can i be able to sit in campus selection??
WHAT IS MEANT BY DERATING OF THYRISTOR?
difference between a diode and thyristor?
Q.1:What protection will be used on HT and LT side of 33/0.4 KV, MVA transformer. Indicate capacities of protective device to be used. Q.2:Which types of back-up protections are used in the power transformers? What do you understand by the term over travel in the relay? Q.3:How star and delta connected winding transformer are provided from earth fault
What are hrc fuses and where it is used?
What happens if the Capacitive Voltage Transformer Primary neutral is not earthed. There is a CVT between Transformer and source, and the CVT neutral of the transformer is not earthed, does it effect the transformer while charging or does it effect the transformer charging process.
what is residuel magnetism. and how order lead acid batteries for 24 volt. emergency lighting system.
how dia of wire and angles are calculated for overhead shielding wire to protect substation equipment from lightening strokes???
What are the special cables required for explosion proof wiring?
State superposition theorem?
hi can any body send me syllabus of rrb electrical section engg... and past pepar also of any board...
Why are the cores of large transformers built up of circular transactions ?
what is magnetizing current test in power transformer
What are the types of feedback oscillators?