how can we change the rotating direction of single phase AC
induction motors?
Answer Posted / sona vijay shah
For changing the direction of rotation of a single phase
induction motor u reverse either starting winding
connection or running winding (but do not change both
winding connection otherwise it will rotate in the same
direction). For this you can simple reverse the connection
of capacitor.
For three phase motor interchange the connection of any two
phase.
Is This Answer Correct ? | 13 Yes | 3 No |
Post New Answer View All Answers
WHAT IS MEANT BY SHEATH VOLTAGE IN 132Kv cable?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
What is meant by full pitched winding?
The loads are connected with phase and ground then why current flow as the loads ?
difference between crane drive and line drive.
How many size of cable required for a 300m long and 30kw inductive lode
with help of neat sketch explain principle of TIG welding process
how to compare with Relay settings for HT< panels, RMU panel, and PSS CSS transformer?? 1) Load amps, 2)Tripping time, 3) CT ratio, 4)Cable size 5) Transformer KVA rating 6) transformer full load amps
how to electrically make connection to ferroli GN2N?
WHat is the general checks required for Dry type transformers
Define Electrical Insulation and examples of Solid,Liquid and Gaseous insulating materials?
What is maximum power transfer theorem?
hi , i have 150 kw loud and we need 50 m cabil,i want to know wich size cabil we use. thanks
what are all the components required to assemble solar panel other than pv cell?
There is air in a room . the top and bottom of the room are at constant temp. T1 and T2. DRAW THE temp profiles if a. T1 greater than T2 b. T1 less than T2