what is the working principle/operation/theory of 3-phase
rectifier power transformer used in cold rolling mills.
Answer Posted / chandresh aghera
the working principle of 3 phase recti is to provide high d.c.
current in rolling millls to rolling material.with hot or cold
rolling.
Is This Answer Correct ? | 2 Yes | 1 No |
Post New Answer View All Answers
difference between Ac and Dc mcb ????
What are safety device in vcb and acb?
How 48-relay (incomplete sequence) functions?
how hazordious area is classified at an oil & gas plant and categorise suitable class of electric equipment in that area like induction motors, LCS, Lighting Fixtures Fluerescent/Flood lights Mercury& sodium lights, J.Bs, Power Cables etc
pls tell me about ups internal connection & we have given only 3 phase supply to ups system how get 4 wire (R Y B N )
Define what is the function of anti-pumping in circuit breaker?
You are of electrical field and you are going for software? Why
Why air circuit breaker off due to power failure?
redundant connection in contactor?
in the case of 6.6kv motor starter combination contain fuses on it VCB. but in 11KV motor starter combination Fuses are not using in it's VCB why?
What is the gross weight to copper ratio in slip ring induction motor of 4000 HP,6.6 kv, 372amp, 992 rpm GE motor.
HOW TO CALCULATE HV TEST VOLTAGE FOR ELECTRICAL EQPT.
Why the earth to phase voltage is high 250 compare to other two phases
DRAW ACIRCUIT DIAGRAM OF 100 KVA 415V/55-0-55V DELTA TO STAR TRANSFORMER
We have received supplies of the ordered material. payments against the supplies also released. Where ST paid 4% against form C. Meanwhile it has been observed that 25% of material supplied was defective. Please suggest whether the issuance of C form from our side would be stopped till settlement of liabilities.