Answer Posted / renjith v.r
The following are to be used
1.Voltage restraint O/C relay
2. E/F relay
3. stand by E/F relay using CT in neutral earthing conductor
4. Under voltage ,over voltage relay
5. Differential potential relay
6.negative sequence relay
7.Vector surge relay
8.Reverse power and Reverse reactive power relay
9.rotor E/F relay
9.High vibration, oil temperature, Overspeeed and under speed alarm trip
Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
What is the difference between a verilog task and a verilog function?
what is the necessity of under ground cables ??
If a air condition consume 2.50 to 3.00 amp then how much it will consume in watts if it is running 10 hours out of 24 hours????
how we control automatic generator i'e with to supply (main supply and local generator) when the main supply was break to supply the local supply automatically to begin supplying power.I now this control circuit is the combination of contactor time delay contactor switch and overload relay .but my question is how we combine those component thank you
What is stacking factor? What is its approximate value?
What is the Diff. btw Manule Pull Station & Manule Abort Station Switches used in FM200 System??
Is there any reason that we get shock on touching phase wire because the earth is at neutral potential? Is there any reason that the earth is at neutral potential because the neutral is earthed in apower station
Why do we require transformer with less specific weight if supply frequency is increased?
in 132kv substation CRT means
What are the advantages of the three-phase motor over single phase motor?
What are the three major categories of error?
can you plz send l&t aptitude questions if available its urgent plz plz plz
what reason of line current and phase current in star connection and line current and phase current not equal in delta connection?
What type of core material is used for metering C.T and protection C.T???
How to determine alternating current frequency?