What are the protections to be used for Generator?

Answer Posted / renjith v.r

The following are to be used
1.Voltage restraint O/C relay
2. E/F relay
3. stand by E/F relay using CT in neutral earthing conductor
4. Under voltage ,over voltage relay
5. Differential potential relay
6.negative sequence relay
7.Vector surge relay
8.Reverse power and Reverse reactive power relay
9.rotor E/F relay
9.High vibration, oil temperature, Overspeeed and under speed alarm trip

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is the difference between a verilog task and a verilog function?

674


what is the necessity of under ground cables ??

1634


If a air condition consume 2.50 to 3.00 amp then how much it will consume in watts if it is running 10 hours out of 24 hours????

1456


how we control automatic generator i'e with to supply (main supply and local generator) when the main supply was break to supply the local supply automatically to begin supplying power.I now this control circuit is the combination of contactor time delay contactor switch and overload relay .but my question is how we combine those component thank you

1514


What is stacking factor? What is its approximate value?

794






What is the Diff. btw Manule Pull Station & Manule Abort Station Switches used in FM200 System??

1397


Is there any reason that we get shock on touching phase wire because the earth is at neutral potential? Is there any reason that the earth is at neutral potential because the neutral is earthed in apower station

1556


Why do we require transformer with less specific weight if supply frequency is increased?

1129


in 132kv substation CRT means

2211


What are the advantages of the three-phase motor over single phase motor?

609


What are the three major categories of error?

678


can you plz send l&t aptitude questions if available its urgent plz plz plz

1651


what reason of line current and phase current in star connection and line current and phase current not equal in delta connection?

1577


What type of core material is used for metering C.T and protection C.T???

1695


How to determine alternating current frequency?

696