if the voltage across the lamp drops by 1%, the power drawn
will be reduced by how many %?

Answer Posted / eee

Power = V(square)/R

If voltage is reduced by 1% power will drop by
.99*.99 = .9801

(1-0.9801)*100

Power is reduced by 1.99%.

Is This Answer Correct ?    58 Yes 11 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

10 tube light connect in mcb breaker.one tube light is fault.so breaker is tribe.how fault is rectified.(using 3wire phase,earth,neutral)

2156


How do you select the pickup value of the relay?

816


explain all the classes with example

1501


how can we save enegry by using VFD for Resiprocating Air compressor which is having more unloading running hours

1795


what's the difference between 'shaft power demand' and 'BHP' , when we consider electrical load list.

1089






How to size Air Circuit breaker (ACB)? What is the most important factors?

1797


Why neutral is not used in three phases dol starter

1421


how rectifier transformer work in electroststic precipetatore(esp?

2101


sourse is 66 KV / 350 MVA, transfarmer is 1000 KVA 6.6 / 0.415 kv, iF fault is 28.75 MVA on 0.415 KV Bus then calculat the Transfarmer Impidance

1654


how 650 volts creates? where is use?

1750


at meter room 50 hrc switch installed,but there are not get earthing proper,so what happen?and 11kv transformer out put going in to hrc main 400a three nog each? so earthing is require for all switch? (some customer made earthing at there home.)

1470


What happens when ac supply is given as excitation voltage instead of dc supply

3140


What is measurement?

755


i have 500 amp inductive load of motors ,,,pleas tell me how can i calculate for capacitor bank for improving my power factor to 99 .....calcullations for capacitor bank,,,,

1155


Transmission through a short line depends on

1680