what is tertiary winding in transformer?What is its purpose?
Answer Posted / anil prajapati
TERTIARY WINDING
In Δ - Δ, Δ -λ and λ - Δ transformers all voltages are balanced and there is no floating of neutral. The floating of neutral is developed in the case λ- λ connection only. The transformers are sometimes constructed with three windings. The main windings are connected to form λ- λ connection and the third winding known as tertiary winding is used to make a closed Δ (Delta) connection to stabilize the neutrals of both primary and secondary circuits. The tertiary winding carries the third-harmonic currents and zero sequence currents (3I0).
HARMONICS are caused because of use of high flux densities in the core. If the core gets saturated during part of the sinusoidal wave, then secondary wave will be non-sinusoidal. This may be due to inadequate core area or characteristics of core material.
Harmonic currents result in:
1. Higher copper loss
2. Higher Core loss
3. More Magnetic Interference
4. Interference with Communication Systems.
Harmonic voltages result in:
1. Increased dielectric loss
2. Interference with communication systems and resonance between inductance of the winding and capacitance of transmission line.
Importance:
Importance of tertiary winding is given below:
1) To supply small additional load at a different voltage.
2) To supply phase compensating devices such as capacitor for power factor improvement which can work at different voltages.
3) In Delta connected tertiary winding reduces Zero sequence impedance and allow adequate current for operation of protective device in order to limit voltage imbalance which may be produced when in balance in load.
4) It indicate voltage in high voltage transformers.
5) It limits the fault current to flow.
Is This Answer Correct ? | 9 Yes | 2 No |
Post New Answer View All Answers
sir& friends i want the collection of recent quetions asked in interview of top most companies please send me on my email san.jsr@hotmail.com
What is advantages of VSCF wind electrical system?
what is the difference between electrical and electronic choke?
IF 8255 CONTROL WORD IS 94H,Tell the chip port work mode ?
How do i carry out or know the vector group of a Dyn1 and Dyn5 transformer
Q.1:What protection will be used on HT and LT side of 33/0.4 KV, MVA transformer. Indicate capacities of protective device to be used. Q.2:Which types of back-up protections are used in the power transformers? What do you understand by the term over travel in the relay? Q.3:How star and delta connected winding transformer are provided from earth fault
working principle a.v.r. ?
hi, i have 3x200KVA and 2 x 80KVA UPS with battery bank of 150AH 68Nos. and 100AH 204Nos., i need to install AC either ductable or PAC type, so can you help me to calculate heat load and capacity of the AC to install.
In layman terms, what is the difference of Dielectric strength and dielectric constant when speaking of an insulating oil
our industries ht line so power fluctation(once drop of power please rectify causes
In the Variable Voltage Variable Frequency Drive, how the Voltage and Frequency varied ? Is it varied in the Inverter part of the Drive ? Please give us supporting document if any.
Why do we use center tap transformer that used with portable tools
how to decide no of electrodes for 1600A LT Main incomer panel
how to calculate the size of the HT cable
What is the working principle of servo motor? And explain it.