Answer Posted / a s nath

Local Breaker Backup (LBB) or Breaker Failure Pretection is
associated with Busbar Protection. If breaker fails to
operate due to its inoperable condition in spite of
operation of protective relays, there will be damage to the
system.This condition is being monitored by LBB relay or
BFR relay (Breaker Failure Relay)and will initiate the
Busbar protection and thus clears the bus.
The LBB protection will operate under the following
conditions:
(i) Lockout relay should operate
(ii)Current shall be more than 20% of normal current rating
(iii) The above currents shall persist after a time,
generally 200ms
When all the three conditions satisfy,it is considered that
the breaker is stuck and LBB protection will operate to
clear the bus.
By A S Nath

Is This Answer Correct ?    117 Yes 8 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

I'm looking for a mnaual set for a Teradyne J750. Softcopy would be preferred but I'll take what I can get.

1746


how does a shunt reactor maintains the bus voltage???

1576


what is meant by carrier aided trip protection in transmission line

3304


what is the responsibility of C license holder in industry?

8537


Explain Active power,reactive power,how its related to each other , & inductive ,capacitive.

1455






Will an earth leakage trip be activated if the component or wiring is faulty on low voltage equipment.Example An electrical Cat Scarer placed in the garden and water gets into the wiring.

1417


what is the mechanism of operation of brushless dc motor why is it more wexpensive then ordinary permanent magnet motors

1505


What is making & breaking current ???

969


How we can calculate the Amps for the cable Ex:- For 1sqmm wire how many amps we can draw (calculation)

2738


if main CT is of ratio 50/5, and meter CT is -/5 what will be overall multiplying factor of meter.PT is 11000/110 .

1154


What is the lockout relay

1061


what is photo voltic cell,& what are the materials associated with that?and any spcifications like volts/cm etc?

1595


l&t switch FN 63 handle position can we change

2107


what are the protecyion of transformer & generators

1460


what is transformor oil gread

1964