What is the avergae difference between OTI and WTI for EHV
Power transformer?
Answer Posted / c.d.elkunchwar
There is no fix differnce as such.Itdepends upon the
transformer tempareture gradiant at that current, specified
by the manufacturer.the difference between ot&wt varies as
per load and gradient.Normally it can be from 12 to 16
degrees at full load.
| Is This Answer Correct ? | 7 Yes | 3 No |
Post New Answer View All Answers
calculate external resistance values to add to the rotor of a slip ring induction motor. STATOR- 415 V, 3 phase delta, 1100 A, 50 Hz, 1490 rpm, pf 0,86 ROTOR - 660 V, 590 A, 50 Hz. STATOR current at each steps STEP1-600A,STEP2- 800A,STEP3-1000A,STEP4-1100A.
List the power rating of any 5 important electrical appliances used in houses.
What is the automatic voltage regulator with servomotor?
Hi Everyone ! My Name is Hakim ullah khan please i need formula of Cable Rating because i want to calculate by self without check any Table Chart... Thank you.....
What is the permissable nutral current of three phase system as per IS standards?
WHAT IS MEANT BY INSULATION CLEARANCE IN VACCUM?
Explain the function and difference of Restricted earth fault, simple earth fault and sensitive earth fault with connection diagram.
Explain what is rated speed?
I AM FROM ELECTRICAL ENGINEERING ? I AM ASPIRING FOR "BHEL".HOW I HAVE TO PREPARE .ON WHICH TOPICS TO BE CONCENTRATE MORE.PLEASE GIVE FULL DETAILS OF WRITTEN EXAM.
What type of core material is used for metering C.T and protection C.T???
Difference between on line capacitor and Station type capacitor
How 3 phase invertor works?
What is core CT & it's function?
WHAT WOULD BE THE FORMULA OF WIRE GAUGE FOR A FULL LOAD CURRENT
what happens if dc supply is given and the remedies for it.