what do you mean by star connection?
Answer Posted / sankara babu
star connection is defined as all the conductors connected to a common point is called star connection .
for the higher voltages we are use the star connection due to the insulation problem.
for higher voltages we use the star-star connections.
on secondary side of transformer we always use the star connection with ground confirm
| Is This Answer Correct ? | 2 Yes | 1 No |
Post New Answer View All Answers
What is the power factor of a transformer at no load?
The advantages of Magnetic flux leakage technique over Ultrasonic technique for non distructive testing of material.
How to calculate impedance volt in Transformer?
what is PDU in transformer?? which company manufacture??
how many types of motor can be used in washing machine
could you measure current in parallel?
Direction of flow of active power and reactive power with logic?
What are the special cables required for explosion proof wiring?
How to calculate the Efficiency of Chiller
how does ELR works? explain
What will be the effect of circulating current in HT xlpe cable when both the armour ends are grounded. Will the termination fils after some time in case of 33 kv supply.
For some transformers we are using solid neutral earthing while some others we are using resistance earthing why ?
While testing a ZCT what parameters have to check or measure?
what is the maintaining Cf in UPS.
How will polarity test of Dy5 Transformer ?