In a 3Ph induction motor(old) 6 wires came out from terminal
& not mentioned u1,v1,w1,u2,v2 & w2. how can find out the
terminals? how can connect to star delta starter??
Answer Posted / raovasuki17
first of all you have to use multimeter to identify the
coil teminals. segregate it in two lines as 2 x 3 . ie top
3 terminals and bottom 3 terminals.
Next take a Small DC power supply with 3 volt and a
milliampere meter( DC ). connect this voltage to one of the
coils with milliampere meter in series( Milliampere meter
should be of center zero type ) close the supply voltage to
the coil with make and break it immediately. observe the
deflection whether it is on forward side or reverse side.
and mark one terminal for whcih +ve suplly is connected as
Start and the other ( _ ve )end as Finish. do this
process for other two coils also. once you know the top 3
start points and finish points of the coil. you are almost
there. now you short ckt all finish ends. you are left
with 3 start terminals. ie your STAR connection.
For Delta connection connect finish end of the first coil
to start end of the second coil, finish end of second coil
to start end of third coil and finish end of 3third coil
to start end of first coil. now you have theree junctions.
now your connection is in Delta mode.
Is This Answer Correct ? | 17 Yes | 2 No |
Post New Answer View All Answers
How to calculate Number of Earthing Pits....???
how to calculate the earth fault current
what is cascade speed control device?and how this device control the speed of motors?
use of choke in APFC panels
In cable sizing calculation (determining the max route length of cable) why we choose the shortest length between cable length of full load current Iflc & starting current Istart?
Is there any specialised book to refer about fault level calculation both in MV and LV side??
what is cathodic protection and why it use in industries?
temp of cast resin 1500kva tx formerwent up to 138.c but came down very fast to about 100.c within 20 mins when load was reduced from 70% to 60%
what are the steps involved in generator load test?
Hello sir i m student of gtu .what is idp.
Differentiate between voltage and current feedback in amplifiers?
We are designer please help me calculate the size of 11kv cables from step up transformer to M.V panel, total load is 5 mega watt distance 900 feet (used aluminum type cables) please provided formula for calculate the cable with example.
Explain cmrr?
What is lc oscillator?
3phase cable calculation formula by motor load