In a Tap changing transformer where is the tap connected ,
is it connected in the primary side or it is connected in
secondary side
Answer Posted / ronak panchal
tap changer is connected at ht side.
its not depend on primary or secondary winding but where the
ht side and lt side is been defined.
if primary winding is ht and secondary winding is lt then
tap changer will be at primary.
| Is This Answer Correct ? | 18 Yes | 2 No |
Post New Answer View All Answers
What is principle of Floroscent tube 36watt.
how we sesign the transformer give some specifion regarding design of transformers
A 15 kw squirrel cage motor having a maximum efficiency of 90% on a continuous full load has temperature rise of 42 degrees celcius after 30 min and 52 degrees celcius after 1 hr under the above operation conditions. a) calculate its final steady state temperature rise on continuous load and the heating time constatnt. b) if the motor is operated on a short load for 9 min estimate its temperature rise. c) calculate the maximum overload that can be applied on a short, 9 min rating so that the temperature rise is the same as the final steady state temperature rise on continuous load.
What is bode plot?
what is errection pcbs?
what causes contact chatter when there is no demand on the air conditioning unit?
Why are short circuit ratings always 16kA,25kA,36kA and 50kA.Who has fixed these?
which is better to use svc or synchronous condenser why ?
what is the efficiency of thyristor
why star point of HT motor not earthed?
what is the maximum permissible limit value of leakage current and leakage counter reading to replace lightining arrester?
how to select overload-relay for perticular motor 1.for D.O.L. starter 2. for Star-delta starter ????
Block diagram of Power line communication?
Factory acceptance test. FAT. For 132 kv transmisstion towers what is that meaning and what are the tests commonly companies perform now days.
How much depth n width required for laying of 1X70 Sqmm Cable in Desert???