what is the difference between 5P20 class CT , PS Class CT
and 5P10 class CT??
Answer Posted / veera
in 5p20 5 is 5% of the 20times of the primary current(i.e)
in case 100/1A CT 20*100=2000A 5% is 100A ERROR AT 2000A
fault cuurent for instantaneous trip this error is
negligible
Is This Answer Correct ? | 67 Yes | 19 No |
Post New Answer View All Answers
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
where solid grounding and where grounding through ngr done and why?
what is the difference b/w absolute encoder and incremental encoder?
My question is whether bellow formula is correct to find bus size for 46kA for 0.5 second & what is RT in bellow formula. formula to calculate the size of busbar to withstand the thermal stresses due to currents with duration of 0.2 sec to 5 sec. Sp = RT( I x I x t) / K Where Sp – is the cross sectional area of bus bar in millimeters. I - is the value of AC fault current. t - is the operating time of disconnecting device in seconds. K – is the factor depending on the material of the conductor, insulation and initial and final temperature. Value of ‘k’ for copper is 143.
What are diffrent type of road taxes?
What are the advantages of the three-phase motor over single phase motor?
what is sevice settings for mccb?How can be it setted?
What is the diffrence (Technical & Construction ) between CBCT & Normal CT?
sir plz send some previous year questions of jspl.
what is Fan Control Cubicle
What is Antipumping Function & If we have C.T how we find the Ratio ?
What is the pro & con of having 11kv & 33kv incoming, and what is the adv & disadv. of converting from 11kv to 33kv.
why the field winding in dc motor is not short circuited eventhough dc supply is applied across the winding
Name a govt approved university which have 100% online engineering course.
how can we phase identification in a distribution line,how we recognise that which phase is coming for a house hold connection.help me............