what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB
(motor protection circuit bracker)
Answer Posted / ashok
MCCB and MCB is for over load protection and Earth Fault protection.MCCB is for heavy duty ie it with stand more fault current.
RCCB is only for Earth leakage protection
ELCB will protect Overload, short circuit,Earth leakage and used where the fault current is more
Is This Answer Correct ? | 43 Yes | 24 No |
Post New Answer View All Answers
what will happen if i connect 12 volt battery with 24 volt battery charger.
What are the different types of controllers?
what is the effect of earth on capacitance in 3-phase and 1- phase transmission line?
if we have a industrial load of 400 kilowatts with 415 volt AC then how much total harmonic distortion (thd%) should be acceptable for steady power system.
what is your aim
Efficient electrical earthing in hard rock area
what is the difference between oil surge relay and buchholz relay.
What is principle of Floroscent tube 36watt.
What is the effect of atmospheric pressure & Temp; on efficiency of motor? Why NGR(Neutral Grounding Resistor) is used in 132/11 KV Transformer & how? What is the use of Auto T/F in Grid Station?
If I want to replace a 26KW Slip ring Motor with a Squirrel Cage motor & Drive (for a Hoist Application). How can I approximate the Motor & Drive HP required in new Setup.
What is the difference between the impedance percent and impedance voltage ?
what is the diference between the 4pole & 6pole DC Motors & what is advantage 6pole over the 4pole ?
PLEASE SEND ME NTPC RELATED INFORMATION LIKE WHICH TOPICS HAV MORE SCOPE,BOOKS TO READ,CUT OFF...PLEASE.mail at thiru.1203@gmail.com
How to calculate Temp from Resister from PT100 equation,
how will reduce the voltage. if 12volt/250ma transformer toreduce 6 volt