Sir We have a REF relay connected to 10MVA(Y-Y) Transformer.on
External earth fault REF relay trips along with earth fault
relay.The REF relay has no complant as we tested relay.Why is
it happening?
Answer Posted / shariff
REF relay shold not operate otherthan its zone of operation
i.e 11kV REFR zone is from 11kV trf busings to 11kV CT
(incomer) and some times PT also if PT is before CT. It is
a mal function only and it can be any of the following.
1) Check the 11kV NCT wiring it may be loose/ got cut in
the NCT wiring box in the yard.
2) The 11kV incomer CT wiring may be loose/ got cut etc.
3) Check the 11kV PT primary resistance it may notbe equal.
Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
IN SINGLE PH TRANSFORMER IF LEKAGE IMPEDANCE DROP IS NEGLECTED ,THE FLUX IN THE MAGNETIC CORE and the lekage flux linking a winding are a)proportional to the applied v to the winding i respectively.
What is meant by time harmonics and space harmonics?
what will be the maximum winding temperature of 6.6kv HT motor 450kw, Full load current 49A. 50Hz Frequency.
Can we check ELCB constantly from R1 to R8 phase in 1 no DB?
can we use trip light with bus coupler?
what is the criteria for selection of conductor used for ehv ac electrical dischrge
dear sir/madam i want to get some knowledge about RRB EXAMINATION(section engineer) 1- what is minimum cut off 2- wht portion is major portion . 3- can any body provide Sample paper. thanks & regards ashish
What is the function of auadag in a cro?
Why different Pressure switch used in marine boiler water circulation system
What do you mean by a phase angel of instrument transformer?
Explain about technical and non technical losses in distribution system?
WHAT ARE THE DATAS REQUIRED FOR PROTECTION AND METERING AND CONTROL AND LOGIC PREPARATION,HOW TO STUDY THE PROTECTION AND METERING?
What is meant by cold loop test in instrument
Ac generato how produce power I need for camplet defination
Do u know any one? how to find out in motor rated amps? formula?