how many earthing required for ups, what should be the
earth voltages
Answer Posted / prabhu
Three Earthings are required.
1. DC side Earthing to avoid the distortion in the line.
2. Equipment Earthing
3. Electronic Earthing for the cards which works in low
voltage.
Where the internal convertor will have the Trafo, that will
be connected for the common earthing.
Both should not common, if Electronic items will get affect
when Ground current flows more than a limit.
Is This Answer Correct ? | 5 Yes | 0 No |
Post New Answer View All Answers
What si the d/f b/w KVA & KWH, kvarh & kvar, kwh & kvar phase voltage & line voltage
what is diff btw electric,magnetic & eletromagnetic field
hello!my name is sheikh iam preparing for indian engineering servieces,please send me the old question papers..to sheikhshaazforjobs@gmail.com
can someone explain that how the speed of the protection system affects the fault level calculation?
Write down the brushes of a de machine.
What is the lower limit of break-down voltage of converter transformer.
2. Modify your design in question 1.a so that the circuit works according to the following function table X Y F 0 0 Clear 0 1 No Change 1 0 Parallel Loading 1 1 Count 3. Design a circuit that detects the pattern 010 in a serial input X considering: 3.a Overlapping 3.b No overlapping
How to select circuit breakers rating eg. if i select a circuit breakers of capacity 40 amps DC with operating voltage 28 volts and if i what to use same circuit breakers for 300 Volts DC application what is the current rating of this circuit breakers.
What are the advantages of using distance protection schemes as opposed to normal overcurrent/ earth fault protection on high voltage feeders.
Why is it prefer to initiate circuit breaker failure by "86" lockout relay not by "94" tripping relay ?!
When lag/lead/lag-lead compensation is employed?
Define open loop control system.
how to CHECK CT AND PT AT THE FAULT OCCUR IN GENERATOR RELAY PANEL .
how do we calculate length of starting time and repeated starting of a direct online starter?
How can get elongation of 2 k.G aluminium, if elongated aluminium dia is 2.5 mm?