Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

How to increase home power factor? Can we connect capacitor
directly? How to select capacity of capacitor?

Answer Posted / srinivasa rao talasila

There is a formula to calculate capacity of capacitor
required for a certain inductive load in KW
KVAR=KW*(Tan of running PF angle-Tan of desired PF angle)
Per suppose my plant is running 0.84 i need to take it to
0.98 at a load of 800KW

KVAR=800*(Tan 32.86-Tan 11.48)
KVAR=800*(0.6459-0.2030)
KVAR=800*0.4429
=354.32 say 355KVAR

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is the Surge for 1.1 Phase Induction Motor(For Eg.1Hp) 2.3 Phase Induction Motor(For Eg.1Hp) 3.AirConditioner(For Eg 1Ton) 4.Refrigerator(For Eg 180Ltr or 160kW) 5.Induction Cooker 4. Ceiling Fan

2063


how to calculate differential current when we testing differential relay..suppose we have 1000kw generator,630amp VCB,what value we should put /inject so that relay trip the VCB? PLLZ justify ur comment

1582


What is the meaning of C1, C61, C91 cable

3475


I completed iti in2004 I was worked in A grade contractor can I get c licence

1729


What is pi controller?

1197


If the Brush of DC motor is shifted by 90 deg, then what happens to voltage and torque? Both voltage and torque are zero. how to justify the answer?

1471


how to get bearing & winding temperature of an induction motor?

2052


what happen when we add mentos in cold drink?& why?

2079


How the setting of the vector surge relay shall be calculated when the relay is to be used for Grid islanding application?

2275


Dears we deal in Chemical are Plate earthing. Kindly call if any requirement and questions. Tech Earth Solutions Mohit Verma 8791071007

1883


how is positive, negative, zero sequence is happen.. how is effect on 3 phase system

1821


although ckt breakers have taken the place of old fuse. But instead of it , these older ones are still used in the industries and homes ? why .... what are their advantages and disadvantages ? which one is leading and winning the race and competition ?

2049


Is it true online ups having bypass mode if it is true then why we called ups because it is interrupting power when goes in bypass mode

2044


what is your majour contributions in your present job

1847


pls tell us AC plant are how do work and parts name with picture

1977