if earth wire is used instead of Neutral wire. Earth wire is
-ive infinit voltage. Then increase in the effective voltage
and then more current will pass. our appliances are meant
for specific voltage grade. this high current will damage
our appliances. usually, you can prove it by using electric
bulb neutral connected with earth wire. and chk the parameters.
Is This Answer Correct ? | 4 Yes | 10 No |