Can we perform parallel operation of two transformers when
one transformer on load?
Answer Posted / vysakh v
when two transformers has to be operated in parallel,their voltage ratios must be the same,Polarities of the transformers must be the same,Percent (per-unit) impedances of the transformers must be the same,Phase sequences and zero relative phase displacement of the transformers must be the same.
Is This Answer Correct ? | 7 Yes | 1 No |
Post New Answer View All Answers
i installed 100kva ups. what KVA genset they should provid in input side? plz any update formula or ans with reason.
standard earthing rating for power line..
Why you want to join non technical field when you are an engineer?
What are the basic elements used for modeling mechanical translational system?
WANTCONTACT NUMBER & EMAIL/ WEBSITE TO CONTACT THE SECRETARY,MADHYA PRADESH LICENSING BOARD(ELECTRICAL),K- BLOCK,3RD FLOOR,SATPOODA BHAWAN,BHOPAL
What is relation between mu(nought) and epsilon(nought)?
1.Can we use 6.6/11KV 300sq mm xlpe 3core cable for LT use (415 Volt). 2. If we use it for LT then what is the current rating
Why is a synchronous motor always star connected??
why ahould you show client/engineer activities clearly on the project plan
WHY MOSTLY Rph IS USED FOR CONTROL CIRCUITS AUX. SUPPLY ?
Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..
In siemens PLC, why do we want to move the data ?
what is a bus post insulator? explain its application in a substation.
two way ckt diagram can be drawn by how many ways? give diagram
how to measure the current by compact digital equipment with dislay which fit inside any equipment