what happens when the transformer is connected to DC supply?
Answer Posted / shyamkr
when dc supply is given to the transformer,since dc can't
produce fluctuating flux ,it will not induce e.m.f in the
primary winding of the transformer.when this counter emf is
not induced in the primary ,the almost full applied
voltage(except little voltage drop in the primary winding
resistance and leakage reactance) is forced in the primary
winding and it may burn.
as far as secondary is concerned ,no emf is induced in it
because emf doesn't vary in case of dc current.
| Is This Answer Correct ? | 37 Yes | 3 No |
Post New Answer View All Answers
why we use four type of phase angle difference between pimary & secondry winding of a transformer & where we use them?
Can we use shunt trip coil instead of trip coil with protection relay for protection?
How can two 3 phase transformers of same KVA and Voltage be connected in parallel?
What are the types of transformers according to the arrangement of iron cores?
please explain to me how to calculate current,voltage,resistance with formula??
What is the Good Earth resistance value of G.I & Cu. Chemical Earthing & Normal Pipe Earthing?
The power supplied to a 33microF capacitor from a 120V, 60Hz source will be
how to calculate the change over time for star delta starter for different KW motor?
What is the function of auadag in a cro?
sir i had plane to do some project with the base of hopkinson test in AC supply its possible
Why derivative controller is not used in control systems?
The D.C. spark test is applicable to single conductor cable & assemblies of insulated single conductor cables without insulation shield,metallic sheath or metalic armor?
witch pump used in wtp
How does HT work & Voltage required?
WHAT IS THE FAULT WHEN 100HP TURBINE MOTOR TRIPS, LIST THE FAULTS AND ITS TRABULESHOOTING TIPS.. MY AUTO TARNSFORMER STARTER TRIPS