Answer Posted / milinda4p

it may vary depending on the requirement of the
motor(whether high torque or high speed).but for an example
in a 3 phase induction motor where an high torque is needed
the rotor windings are first connected in star to get rid of
the large current(inrush) at the starting. & then after
starting it is set to delta to have a large current (because
then the voltage across a single winding is square root of 3
times that of in star=> square root 3 times larger current
in single winding) (to have a higher torque)

Is This Answer Correct ?    3 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

A commercial Building is designed with 14th floor levels with indoor substation of three phase transformer with rated capacity of 1000 Kva.The transformer delivered 65% of its rated capacity at 0.67 power factor lagging.Because of low power factor, the power customer was penalized and certain cost was charged accordingly based on every point percentage lower than 85%.This situation may repeatedly happen on the succeding energy bills of power customer.The power customer is desired to improve its historical power factor of 0.67 lagging and no further penalty be impose by the local power company on the next bill. Q: Identify the appropriate solution you want to offer to Client?.Justify SCIENTIFICALLY and MATHEMATICALLY the principles behind the solution.

1338


if negative of DC supply used and positive is grounded through EGB, and if ELCB used in the system then is it sense the positive volatge and get tripped is it possible?

1274


what is control supply rating of a machine

1486


Differentiate between ideal and non ideal current sources?

648


How to define Kirchhoff current law and voltage law along with simply examples.

1216






Is it posible to instal one more SMDB from the existing SMDB and is it practical.

1593


what is the transiant condition in alternator? and how it can be prevanted?

1495


The ripple frequency in output of fullwave bridge rectifier is a. Half the input b. Twice the input c. Same as input

1808


hi, in the event earth grounding is not available in a project, is there any other way to make the elcb work? fyi, i have an instant water heater (6.5kw) installed, however if there is grounding in the heating element inside the heater assembly, i will get grounded. thank you in advance to those who will answer my question.

1512


Why is the air gap between the pole pieces and the armature kept very small?

889


what is the meaning of 0.5ohm Resistance

1398


Why to keep capacitor bank off while generator running.

1290


Pls Breifly explain about UPS (Inverter,Reserve,Rectifier,Float voltage,Boost voltage).

2299


how power is generated,and transmitted to our home..pls explain briefly in simple words.

1771


what is the minimum requirement gigaohms for the insulation test using 5kv in 300mm xlpe cable

1518