how can we avoid magnetostriction in transformer?describe
the suitable methods.
Answer Posted / adil akhtar
we can avoid magnostriction by (1) using the difrent type of
alloy of iron in the core sheets.(2) using the slicon steel
in the core.(3) leminating the magnetic alloy when their
surfaces are abraded.
| Is This Answer Correct ? | 11 Yes | 3 No |
Post New Answer View All Answers
what irequirment need to be followed when working on live equipment
How PADO software increase the efficiency of power plant?
WHY TERTIARY OF POWER TRANSFORMERS IS LOADED WITH EQUIPMENTS LIKE CT,PT,ISOLATOR AND CB
What is the reason behind current flow(20 A) in amain earth cable of an SMDB? Is cuurent flow(45A etc) through a neutral cable acceptable?
Usually in the L & T make MCC feeders' power circuit,we have BMR after the MAIN CONTACTOR.,can we interchange their position, keeping the control logic same???
What is the function of retrip in busbar?
what is the function of impulse relay
What must be the minimum distance maintained between 2 Generators as per International standards?
PLEASE SEND THE PREVIOUS YEARS QUESTION PAPERS OF RRB JUNIOR ENGINEER-ELECTRICAL
if sf6 gas low in gis what will happen
best manufacturer for busbar for outdoor switchyard having double bus bar scheme, can any one share technical specification of busbar. 132kv voltage ?
How would your past experience translate into success in this job?
What is the rating factor for copper cable ( Specific value according to the type of laying ) & the voltage drop?
when it is possible kvrah lead & fundamental kwh be equal in electonic trivector meters (3 ph)
Explain M Var? Which types of problem occurs when reactive power increase at the time of full load of plant and at the time of synchronize of plant?