What is the difference between CRNO and CRGO in an
transformer and what is the advantages of these two.
Answer Posted / rajesh babu.d
CRGO - Means "Cold rolled Grain oriented" Silicon steel.
The line itself states that the distributed grains are
oriented through cold rolling process, which gives you
minimized losses.
As the CRGO material having low loss values, these material
is universally accepted to design the Core Structure of the
Transformers, in which losses play a vital role.
CRNO - It is Cold rolled non grain oriented, that means in
this the grains are distributed and not oriented in the
soecific structure.
this process doesn't cause to minimise the loss, and hence
these are having high loss comparitively with CRGO.
These material always finds the application to design the
core structure of any electrical equipment, in which losses
are not concerned to a greater extent.
Is This Answer Correct ? | 28 Yes | 6 No |
Post New Answer View All Answers
formula for calculation of switchgears(i.e. contactor, fuse, cb, relay etc.), if load current is given?
why burdens of VTs is more than CTs?
what kn of disc is used in 33kv,132kv,220kv,400kv,800kv transmission line
Is a direct shorth ciruit on a branch MCCB in a Low Voltage Switchboard a correct means of tesing the performance for discrimination?
How many types of colling system it trformers?
How to select a transformer group to connect a 0,433 KV generation with 33 KV grid in bi directional flow of current
how to calculate the lightning arrester conductor @ no of earth pits required
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
1)How much current can a 3-1/2 core 100 mm wire carry? 2)What are the special cables required for explosion proof wiring? 3)In case you do not have coal and salt for earthing, how can you achieve good temporary earthing? 4)One horse power single phase motor is more likely to get hot than a one horse power 3 phase motor. Is it true or false, if true why? 5)What are the different types of soft starters for large motors?please explain?
dc supply given to dc generator winding.how is possible? my knowledge is saying the winding will burn. please reply.
What are the advantages of hydropower?
hello everybody. what does an abnormal stator winding impedance or dc resistance show? thanx
Draw a block diagramof Three UPS systems connected in Parallel mode?
A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e in running condition) whether there is actual earth fault in rotor or not.
How to calculate the External Resistance required for 60HP slipring motor in case no any data of the Motor is available???