what is DG synchronization panel
plz explain the working!!!!!!!
Answer Posted / pillay
A DG SYN PANEL IS FOR synchronising two or more DG into the system.
when only 1 DG is used there is no use for the syn panel.
When the second DG is started and brought to operating
voltage and frequency it needs to be paralleled at the right
moment in order to be able to share the load of the system.
The syn panel takes care of this, after "the" synchronising
the panels duty ends till another syn is necessary.
Is This Answer Correct ? | 54 Yes | 18 No |
Post New Answer View All Answers
What is the difference between AC and DC injection methods for rotor earth fault protection
What is PQA???Applications........
design a LV scheme for a 15 storied building?
Which device is used for the source of emission of electrons in a crt?
we have provided 30 nos. relay contacts in panel.I want to know how do we do the numbering for the relay contacts as per any applicable standards
Why are the laminations insulated from each other?
Can 33kva/415v transformer be run underground? If the answer is yes why and if the answer is no why?
why the name trunking bus PT
what is the grounding Calculation formula? spouse i want to provide grounding to 3phase 18kw motor or i want to provide ground to 3phase 10kva dry type transformere or you give me any exemple...... Thanks.
what is calculation mathod/formaulla for deciding Size of busbar (Copper/ aluminum)for L.T. panel on Various Fault level like 50kA,25kA,10kA
what is the defination of Cable database? What are the points are considered while preparing cable database? Is there any sample available for cable database?
what is physical distance of isolator to VCB in 33/11kv sub stations
what is the importance of Partial Dischage test for Electrical Equipments
Single line digram for 11 kV to distribution use go,la and do
Why do we avoid electrical conduits in floors at apartments?