what is the use of vector group in transformer. means what r
the application of various vector groups?
Answer Posted / paul
By having multiply vector groups, you have the ability to parallel 2 or more transformers with with different vector groups by altering their connections.
EG. you can change a Yd11 into a Yd1 by changing the HV and LV phase sequence from positive to negative.
So with that in mind a Yd1 can be converted to a Yd5 if required by placing L1 onto L2, L2 onto L3 and L3 onto L1. The reason for the 4 vector group shift is down the fact that you have rotated each phase by 120 degrees
| Is This Answer Correct ? | 0 Yes | 3 No |
Post New Answer View All Answers
An impedance of 100 ohms resistance and an unknown inductance is connected across the capacitor. The resulting impedance is a pure resistance of 500 ohms ifω = 10^5 rad/sec. calculate the values of inductor and capacitor.
Define piezo-electric effect?
how to select the double earth conductor if 21A full load?
what is the difference between "Rotary bypass isolation switch and Normal bypass switch" pls share indepth techs?
Explain what cmos is and its benefits?
what are pilot cells
how to extend relay operating timing in 24V dc relay card (without using Timer )
how to find ratio of CT & PT in 66/11kv 12 mva supply system ? explain with calculation.
Basic motor transformer generator
what do u understand about FACTS? how they are useful?
How to design harmonic filter at the project stage without nowing the harmonics levels
how to check avr of dg set of 125kva
What happen when neutral point connected to core balance current transformer? (Neutral point of an alternator of a 180KVA DG. Neutral point connected to CBCT means enter to the CBCT)
What is the rating of circuit breaker needed for 300 KVA load in 33 KV supply line in a transformer of 33 KV / 415 Volt ?
why 5kW motor becomes unbalance if its relay trip 1st time and its set value is 7.0 A