1 Ton = ? amperes & power.
How much power 1.5 TON split AC consumes in an hour at 17
C , 26 C & 28 C (thermostat' temperature).
Answer Posted / randy
BASICALLY, 1 TON = 12,000 BTU
1 WATT = 3.412 BTU
THEREFORE: 1 TON = 3,516 WATTS = 4.713Hp
CURRENT (Amp) I = Power (Watts) P /Voltage
(volts) V
I = 3,516Watts/240Volts
I = 14.65Amperes
The ans: a)P=3,516Watts
b)I=14.65Amperes
| Is This Answer Correct ? | 77 Yes | 99 No |
Post New Answer View All Answers
Why squirrel cage motor can only use with low starting loads ?
how give earthing conection to household equipment?
do anyone out there know where to find a compleete list on acronyms/abbreviations used in offshore electric engineering. MCB - Micro Circuit Breaker, MCCB-Mouldes Case Circuit Breaker, ELCB-Earth Lekage Circuit Breaker, ELMCB- etc.....
What is the classification of hydro projects based on installed capacity?
how to commissioning the genset with amf panel?
What is the permissable nutral current of three phase system as per IS standards?
what is the relation between size of the anteena and wavelenghth of radiated wave
HOW CAN WE DECIDE THE SUPPLY VOLTAGE FOR MOTOR ACCORDING TO ITS RATING(IF ANYONE KNOWS GIVE IT WITH EXAMPLE AND ITS CALCULATIONS)
what is the prosses for getting of 33kv licence (i have completed my engineering degree & working in 33kv substation for contract basis )????
How to convert a two phase power into a three phase power in induction machine?
why does a dc machine has high efficiency while working as a generator than as a motor ..
what is magnetizing current test in power transformer
The D.C. spark test is applicable to single conductor cable & assemblies of insulated single conductor cables without insulation shield,metallic sheath or metalic armor?
what is meant by neutral compensation factor and where it is used
What descriptive information does the NEC require to be marked on all conductors?