Why in DC drive u r using in Klin operation in Cement Plant?
Answer Posted / deepak gade
Hi
Kiln need high starting torque,and DC motor have capability
to produce high torque for kiln rotation
Also dc drive have speed accuracy, we can increse/decrese
speed upto 0.1 v dc
Is This Answer Correct ? | 16 Yes | 0 No |
Post New Answer View All Answers
In radial network the source is fed from 1 end both ends at central
What are the material used for resistor?
If we use 250A MCCB as a incomer in Control panel for a fault level of 50kA for one second ,assuming temperature rise from 85 Deg. to 100 Deg , Then what will be the Aluminium Bus-bar size for 250A MCCB? Explain in detail.
What is polar plot?
what happen if the load connected to the induction motor is taken away? the same question for synchoronous generator in synch i think that the the exitation voltage will appear on the terminal only if so plz answer me
What it the purpose of parallel phasing transfomers??
where the lexical paramater will use in fron end?
Can we use shunt trip coil instead of trip coil with protection relay for protection?
How do I calculate/select Droop CT ratio for various capacity of generators?
can u give me a brief idea about power line carrier communication ??
What is electrical grounding?
How can we convert 11 kv to 440 volt without using transformer ?
What is the one main difference between ups & inverter ? And electrical engineering & electronics engineering ?
standard earthing rating for power line..
Why can't we parallel Voltage transformer secondary circuits?