what is pressure relief valve in D.G ?state its function?
Answer Posted / dinesh (techie.dinesh@gmail.co
whenever the pressure in the transformer tank increases, the
pressure is released by PRD. PRD reduces the pressure by
splashing the oil outside the tank, i.e the PRD has a preset
value, if the value exceeds beyond the preset value, the prd
comes in action.
and when the PRD reduces the pressure, the vertical
flap/flag mounted on the PRD raises. although the pressure
is reduced, the flap wont lowered, it is used to indicate
the supervisor/operator that the pressure value has
increased. once the operator get noticed, he will manually
lower that flap
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
what maximum range of star & delta in hp or kw ?
How Can you do Maintenance of ACB of 2000Amperes
What Maximam Gap Taibaar & Bush
What type of fittings and electrical accessories can be install in radiation area ?
Mention how NPN and PNP transistor works?
best manufacturer for busbar for outdoor switchyard having double bus bar scheme, can any one share technical specification of busbar. 132kv voltage ?
What is the practical way to calculate the cable size for known ampere load?
how to test reverse power trip?
what is difference between line differential and transformer differential?
How can we calculate cable size in Low voltage & high voltage
How to calculate loses in transformer of 160 KVA ?
If I have Energy Meter Ratio as 100:5 & Also I have CT Ratio as 50:5 then what will be my multiplying Factor(M.F.)
what are the specifications we must look at to select a relay for any capacity motor?
How you give clearance to a spare feeder.
IN electrical field, WHAT ALL THINGS THE CUSTOMER WILL ASK WHILE ORDERING FOR LT PANEL (ALL TYPES OF LOW TENSION PANEL)