Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

What is the role and reponsibilities of Electrical
Engineers in construction field?

Answer Posted / p.k.chadhar

in the construction field the roll of electrical engineer is
as follows
1-he has to see the basic design engineering of the project
2-detail engineering with safety factor in the design .
3-basic & detail engineering for provision of earthing pits
of electrical intallation.
4-design for illumination of different area and lux calculation.
5-cable size calculation cable scheduling &its route
selection ,over head or under ground
6-proper protection system for all electrical installation .
7-design for fire alarm &detection system &so many more
which i am not writing here

Is This Answer Correct ?    112 Yes 14 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Power factor =1.000 at factory in supply. However, PF = 0.8 at motor end. Current = 100 Amp, Voltage = 400 V. What is the power distribution loss? Can I reduce it by adding capacitor at the load feeder?

2043


Explain the working of any one cutting machine

1110


When steam condenses and becomes water at the same temperature, the specific heat for the process in kJ/kg k is

1142


What should be the magnetic balance test values for a 3 phase delta/star connected single primary dual secondary winding transformer (90 MVA / 2 X 45 MVA TRANSFORMER)

1925


what is the formula to calculate voltage drop/loss on 66KV Transmission Line?

3702


We have a distribution transformer of 750KVA/11kv/440v and an AVR (Servo Stabilizer) of 750KVA on the LT side of distribution transformer. Also we have an ACB of 1200A on the output of distribution transformer (that is on the input of AVR). We want to have an MCCB on the output of AVR. What should be the rating?

2106


Good morning: I'm looking for some informations about the OLTC or the LTC: I wont to know what the function of the tie-resistor in during the operation of reversing/coarse operation Cordially

2012


Pls Breifly explain about UPS (Inverter,Reserve,Rectifier,Float voltage,Boost voltage).

2791


How to work E.L.C.B and how to connect in circuit.

2018


Difference between field rheostat and armature rheostat.

1234


I have one ct of ratio 3000-2000/1 Amp its knee point voltage mentioned on name plate is 500-333/30mA-50mA at Vk/2. in secondary box there is three terminal named 1S1, 1S2, 1S3 then on which terminal obtained the knee point voltage ie 1S1-1S2 OR 1S1-1S3 & also specify the knee point voltage for the ratio 3000 from name plate.

2454


For an induction motor wat is the loading/unloading cycle duration or interms of L/UL ratio/ percentage?

2110


FOR 16/20 MVA 132/33 KV ONAN/ONAF TYPE TRANSFORMER IT IS DESIGNED FOR 16 MVA WITH ONAN CONDITION.IT BECOMES 20 MVA UNDER ONAF CONDITION.LOAD LOSS IS GUARANTEED FOR 65KW AT 20 MVA AND % IMPEDANCE 13.75. PLEASE TELL US AT WHAT LOAD LOSS AND % IMPEDANCE IT SHOULD BE DESIGNED FOR 16 MVA AND WHAT WILL BE ITS EFFICIENCY AT 20 MVA?

3406


if i am in front of transmission line how to know that current direction without any equipment

1778


If one tertiary phase i.e. R,Y or B is earthed of a loaded type tertiary delta connected (Without load)of a power auto transformer, what is its advantage/disadvantage?

2090