What is OLTC in a transformer, specify its fuction.
Answer Posted / shreenidhi
OLTC(on load tap changer)is a mechanism used in transformer
for changing the tapping position on primary side(HV)of
transformer.For any installation mostly in industrial areas
and rural areas the voltage on HV of the transformer will
not be 11kv(taking an example of 11kv System)and
correspondingly the output will not be 433v.To maintain a
constant 11kv/433v the tap changer on the Primary/HV side
of the transformer is either raised or lowered to maintain
constant 11kv input to transformer.Normally it is raised or
lowered in steps of 2.5% of normal KV value.
| Is This Answer Correct ? | 12 Yes | 7 No |
Post New Answer View All Answers
State and define norton’s theorem?
draw the block diagram of fire alarm?
what is the function of impulse relay
If a current -8+6sin6t is flowing three ammeter, one is a centre zero PMMC meter, one is true rms meter and one is moving iron meter. What are the reading of these three meter respectively?
What are two contours of nichols chart?
What is the physical significant of power factor?
During Starter Panel Com missing I Found The Main Incomer 40Amp MCB 10KA Trip When Motor Change Star To Delta Motor Rating 20HP BUT When We Use Same MCB To Other Motor It Does Not trip Or What Is Necessaries for Star Delta Starter MCB SFU MPCB OR MCCB And What are The Breaking Capacity of MCCB in the Motor above 15HP
Explain using drawings what is reverse PID action w.r.t PID controllers.
1600kva capacity Transformers how the bucholz relay,Oil temperature,winding,surge relay relays setting are to be done
When a single pase capacitor run motor- run on 230vac and Case(1)run with 8 Mfd 250 vac.capacitor , Case( 2) run with 8 Mfd 400vac capacitor. What is difference between both case regarding power ,efficiency etc?
1.Can we use 6.6/11KV 300sq mm xlpe 3core cable for LT use (415 Volt). 2. If we use it for LT then what is the current rating
If I want to replace a 26KW Slip ring Motor with a Squirrel Cage motor & Drive (for a Hoist Application). How can I approximate the Motor & Drive HP required in new Setup.
What's mean HVF & HAF in Vacuum Circuit Breaker?
hey guys i scored 910 on GRE and 67 on TOEFL respectively.I have an aggregate of about 74%in my B tech.For which colleges should i apply for an MS program in electrical engineering.I am looking for colleges in NJ,SC,NC,GEORGIA, NY. Please reply with a good response.....
what is The difference between national electrical code and I.S.Code (electrical) and what is the value of NEC in electrical engineering field