what type of relays used in transformers?
Answer Posted / sethu siva & mainkandarama
1)Differential protection (If transformer is more than 5
MVA :As per IS 2026)
2)Restricted earth fault protection
3)Stand by earth fault protection
4)O/C & E /F protection (if required)
5)Over flux (V/F)
Auxiliary protections
1)B' relay protection
2)PRV
3)Oil temp. high trip
4)Winding temperature high trip
5)OSR
Alarms:
1)Winding temp. high alarm
2)Oil temp. high alarm
3)MOG alarm
Is This Answer Correct ? | 15 Yes | 1 No |
Post New Answer View All Answers
how the B-H loop obtain under the static condition
What is the Temperature to be set in Thermostat provided in Marshalling box of the Transformer / Motor.
What are the advantages of instrument transformer?
What should be the protection scheme for a 15kw, 3-phase motor working in a lathe machine.
We have 750KVA DG set, we want to introduce REF relay with 1250/1A,CL PS,Current transformers.The lead distance of 2.5mm copper flexible cable from CT to relay is around 5mtrs.We would like to know the knee point votage(VK) & IM calculion for CT's
State and define ohm’s law?
do we use neutral grounding for resistive balanced load? if we use what happen?
what is meant by CT`s saturation ? Can we use Metering CT`s with Protetection CT`s ?
How to reduce the static electricity producing in solvent room? By P.D.Patil BioCon
An automatic water heater is an example of which type of control system?
In general bus riser follows the bus section in SWGR. What are impacts if bus section follows bus riser?
what is a composite error in current transformers, why occurs & in which it will occur i.e, either metering ct/ protection ct
please tell me how a surge protector work on a DC 48Volt.? please describe briefly.
Is phenomenon of resonance is harmfull fr the machine? if not or if yes please explain it?
how to increase senstivity of ct