what is the formula to calculate kva genset required for a
given load in kw.

Answer Posted / virendra

Kva Required is = KW/0.8( Power factor )
& as the DG set is prefered to run at 80% load of the total
capacity then the Rated capacity is KVA/0.8

If the load is 100 KW rhen KVa is 100/0.8 = 125 KVa & the
rated kva is 125/0.8 = 156.25 KVA say 160 kva D.G set is
required.

Is This Answer Correct ?    34 Yes 6 No