what is GRR(Grid Rotot resistance)?Why it is used beside of
LRS?

Answer Posted / rajesh ku sahu

GRR(Grid Rotot resistance) is a resistance box which is
used for speed control of slipring Induction motor & save
the power.The Induction motor having high starting torque
needs resistance in rotor circuit by the use of GRR we can
add the resistance in the circuit & increase the slip so
torque, ones motor will start we reduce the resistance of
GRR by Contactor,and at full speed shott all resistance.
LRS is used where no speed control is required only high
starting torque is required.

Is This Answer Correct ?    29 Yes 6 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Currently what is the highest capacity (MVA) of SPPg generator available in the market?

1329


How to calibrate or test an LT Air Circuit breaker 440 volts, 35 KA, 800 Amps ?

2119


in battery charging room we find two fuses (one in positive other in negative cables ).why it is so?one fuse is ore than sufficient?

1803


The loads are connected with phase and ground then why current flow as the loads ?

1480


Some times to change of DOR of a motor, interchange of R & B is not effected and RYB take same current, but interchange of R&Y is effected ie change the DOR. My doubt is what is the problem in motor and how it is happen.

1541






2. What are the parameters of EHT sub-station?

1840


Why is voltage is required to be within permissible range for an electrical equipment?

1266


What happen when neutral point connected to core balance current transformer? (Neutral point of an alternator of a 180KVA DG. Neutral point connected to CBCT means enter to the CBCT)

1839


how is find out kwh step by step

1324


What is the most accurate way of testing ELCB?ELCB is better than RCD?

2876


What is advantages of VSCF wind electrical system?

1908


Which device is used for the source of emission of electrons in a crt?

731


why we change the direction of winding in rotor ?how we make the north and south pole?

1582


WE know that for Inductor X=2pifL,In DC f=0,then X=0 so,V=IX=0;But In the DC excitation of rotor of AC generator,DC motor field coil which coils are inductor so why does not applying DC voltage short the rotor coil of AC generator and field coil of motor?If it would then DC source might be damaged but it is not happened. Why does the strand conductor of Electrical power transmission line make twist?

3812


for a 500 KVA connected load, I calculated 30% of capactor for power correction. Even after using 225 KVR capactor PF is not improving. What could be reason for low Phase correction factor?

1530