What are the differents between Breaker & Contactor?
Answer Posted / rajesh ku sahu
Basic difference between circuit breaker and contractor is
That, A circuit breaker can make, break and carry current
in all conditions i.e normal, overload and short circuit.
It will protect the system from over load, Earth fault &
unbalance as well as it has different load & trip setting
and it don’t want any fuse back up. That was not inbuilt in
contactor. A contractor can make, break and carry only in
normal and overloaded condition not in short circuit
condition. Also, Contractor are always backup by HRC fuse
where as there is no need of any backup in circuit breaker.
For frequent operation, contractor is more efficient than
the Circuit breaker.
Is This Answer Correct ? | 5 Yes | 2 No |
Post New Answer View All Answers
Why neutral cable carry current.
In a large office how do we calculate required number of light fittings, assuming fittings are 4x18W or 2x36W fluorescent fitting ?
What do you mean by Stimulastion Test in Diesel Genarator / Why & when it's conducted ?
HOW can i REuse the fused MLL LAMPS & GLS LAMPS at our factory
What is core CT & it's function?
how does a liquid starter reduce the starting currents?
In CTs tan delta point should be earthed , what is the reason behind it?
How many types of colling system it trformers?
why the pf of semiconductor device is improved the electrical devices
Mention the methods for starting an induction motor?
what is vA rating and class of a ct.
why chock were used in old tubelights but are not newest tubelights?
what questions will be asked for 11/33KV licence interview APSEB hyderabad. Can any one share question and answers.
what causes contact chatter when there is no demand on the air conditioning unit?
Mention the disadvantages of low power factor? How can it be improved?