how to calibrate a control valve?
Answer Posted / azmat
To calibrate a valve first check the input signal range if
it is 0.2 to 1.0 Kg/cm2 or different.
Calculate the span ( Difference between higher limit to
lower limit=1.0-0.2=.8 ) Now divide it in four equal parts
that is 0.2 Kg/cm2 this is 25% of the span.
Now check the valve travel like 2 inches, 3 inches or any
other value Divide it in four equal parts 25% of the travel.
Apply 25% of the span value+ 0.2= 0.4 Kg/cm2 it is 25% of
travel and apply full span value and see you get the
complete travel if you find difference adjust the spring
accordingly.
Is This Answer Correct ? | 82 Yes | 10 No |
Post New Answer View All Answers
How the sizing of the analog signal cable is calculate?
what is function of sensor, and how is it work , explain with difination
Which type of diagphram use in costic line,DM water line,natural gas line,oil line?
How addressable fire systems work? Pl. send details with architect.(Loop), also send details regarding Gas system. Pl. help me.Thanks
i want to know the interview format fot gail, instrumentation. pls answer me in habib.sami1003@gmail.com
please send me some question papers of HPCL aptitude test ?? please send it to bipinb.28@gmail.com ...
what is interface level and how it is calibrate?
how to calculate range of level transmitter?
How an rtd work, and what volts/current goes to a rtd to measure the resistance?
how to calibrate and troubleshooting of leveltroll?
can any send me a forbes marshall dtron 316 manual
What are different type of instrument cable
HOW TO CALCULATE ACCURACY OF AN INSTRUMENT. WHICH IS COMPITABLE FOR USE.
how many type of plug are used in pneumatic control valve,name them.
What is PDS and PDMS ?