What's the part of OTCC in transformer?
Answer Posted / sudhakar ghait
OLTC - ON Load Tap Changer. When primary voltage low/high
in that condiction we will maintain our secondary voltage
by using our transformer's OLTC
| Is This Answer Correct ? | 6 Yes | 1 No |
Post New Answer View All Answers
Write a note on Treatment for electric shock.
"TRANSFORMER MODELING AND ANALYSIS" MEANS WHAT AND WHICH TOPICS U READ IN THIS
why the making current is more than then the breaking current and if its true then its about a controling circuit or breaker power contact points
5- What is the task (function) of the excitation and isolation transformers in power plant? 6- What is the task (function) of LCI (A), LCI (B) and LCI (COS) in power plant? : LCI (A) and LCI(B) are load commutating inverter for generator turbine starting. , LCI (COS) is load commutating inverter change over switch
how ct burden,magnetising current,ratio and knee point voltage are related & derived
What does the term supermesh means?
how to copy from plc ge fanuc versamax series,all input and output, adress, and printout.
Q.1:What protection will be used on HT and LT side of 33/0.4 KV, MVA transformer. Indicate capacities of protective device to be used. Q.2:Which types of back-up protections are used in the power transformers? What do you understand by the term over travel in the relay? Q.3:How star and delta connected winding transformer are provided from earth fault
Merits & Demarits of Oil circuit & Air circuit breakers ?
What is the difference between PLC and Embeded system
Why mostly the HV side of transformer has Delta?
Define peak overshoot.
What do you mean by passive circuit elements and why these are called passive?
how to calculate transformer turn primary & secondary side 11kv to 420v
what is the diference between the 4pole & 6pole DC Motors & what is advantage 6pole over the 4pole ?