what is the difference b/w circuit breakers and relays?
Answer Posted / inderpal
Circuit Breaker is a protection device which can intrupt
the fault current, CB has high fault level with-stand
capacity (kA). Relays are also used in protection circuit
but relays cannot with-stand high fault levels. Relays are
generally used as sensing element to open the circuit
breakers.
Is This Answer Correct ? | 16 Yes | 0 No |
Post New Answer View All Answers
any body,pls tell me how to done relay coordination ? how to coordinate by TCC curve?how to read the tcc curve?
How do I calculate a WTI CT ofa 1250kVA 6600/400V transformer
how to select the double earth conductor if 21A full load?
write a c++ code that receives an integer number and display the sum of the number and its revers integer?
Why in metering Ct for ammeters ct secondary side is grounded for each Ct but not in case of CBCT (Core balance current transformer)..kindly some1 highlights the reason..is it because net flux is zero?
how to get bearing & winding temperature of an induction motor?
How does a digital electronic meter work??????
can we install HT panel & LT panel side by side or how much clearance is required ?
Define step response?
Where voltage are high and current to be interrupted is low the breaker preferred is:
When is lag lead compensator is required?
i have 3500 amp load and select current transformer and perches.how i calculate .please understand
FOR 16/20 MVA 132/33 KV ONAN/ONAF TYPE TRANSFORMER IT IS DESIGNED FOR 16 MVA WITH ONAN CONDITION.IT BECOMES 20 MVA UNDER ONAF CONDITION.LOAD LOSS IS GUARANTEED FOR 65KW AT 20 MVA AND % IMPEDANCE 13.75. PLEASE TELL US AT WHAT LOAD LOSS AND % IMPEDANCE IT SHOULD BE DESIGNED FOR 16 MVA AND WHAT WILL BE ITS EFFICIENCY AT 20 MVA?
draw singleline diagram of star to delta and dol starters