Why the Potential transformer Primary in connected to Earth?
Answer Posted / koodalingam
To protect the primary winding of the potential
transformer.If you not earthed the system,the unbalance
voltage will appear between neutral and earth.This voltage
can damage winding.
Is This Answer Correct ? | 10 Yes | 1 No |
Post New Answer View All Answers
"TRANSFORMER MODELING AND ANALYSIS" MEANS WHAT AND WHICH TOPICS U READ IN THIS
what percent do you derate your copper wire when you change from copper buss to copper wire
while starting a liquid starter ,is there any volage drop on water/soda on tank.can we touch the tank on starting?
1)how to reduce the value of tan delta of trasformer and CB,bushing,CT&PT,CVT ? 2)how to reduce the resistance of CB contact and its operating time? 3)plz.....send me the project report on conditioning and monitoring of substation equipment on my email id (gusaiyogendra03@gmail.com)
What are the difference between normal application Transformer and Solar application Transformer?
what is the IPC ? & what the uses ?
In between UPS out going changer over switch and ups raising main input, both side cable gland producing heat but the cable doesn't get heat,Why?
diff b/w normal grounding and resistance grounding
we need a ntpc previous papers
How many double suspension hardware fittings are required on a double circuit transmission tower?
what rectifiers is and what are the types of rectifiers?
How much earthing frequency is capable?
how to measure earth resistance of a substation
how to calculate units consumption for a 12 hp motor /hr.
Explain the term parallel path in dc machin ?