How many earthings are provided for a 250KVA distribution
transformer?
Answer Posted / vilas
As per rules four earthings are required.
two for neutral. star point
Two for the transformer tank i.e.body of the transformer.
| Is This Answer Correct ? | 12 Yes | 1 No |
Post New Answer View All Answers
Can anybody inform me about the pattern of ECIL GET( Graduate Engineers Trainee) interview for Electrical students? Will there be HR round as well? I thought of preparing for 2 to 3 subjects thoroughly. Will it be sufficient? Please share your thoughts.
What is current divider rule (cdr)?
quantizer means?
How to set the relay,,??
We have given to 3phase supply to ups system & how can coming netural
why do you add the load short circuit impedance when considering short circuit amperage. It seems that you should only consider supply. If you need to consider loads and you don't know what loads are to be added , what would be a good sub-transient reactance rating for the loads?
How many points does a Circuit can have?
how we can calculate 2 phase welding transformer rating or total power?
A 50Hz,4-pole,3-phase,star-connected synchronous motor has a synchronous reactance of 12ohmsper phase and negligible armature resistances.the excitation is such as to give an open-circuit voltage of 13.2kilovolt.the motor is connected to 115kilovolt, 50hertz supplying. what maximum load can be the motor torque,line current and power factor?
circuit diagram of trip circuit supervision relay
what are problems caused by the pdu in rack server
What are the site acceptance tests for power cables, DG Sets, LT panels & 30kVA UPS ?
What is the important precuations need tocarried out while working with Electrolite in Battery PM?
how to calculate micom relay earth falt time and current sertting
What are the different types of transformers?