how would you come to know if a transformer is double wound
or auto? note that there is no tag. you are given only a
multimeter.
Answer Posted / matthew
On an autotransformer there is a physical connection
between the primary and secondary and the voltage variation
is not much so the resistence steps are less. The opposite
is true for double wound transformer.
Is This Answer Correct ? | 7 Yes | 0 No |
Post New Answer View All Answers
High speed earth switch operation with diagram
what is earth pit , how we can measured it, what earth rods reference
What is the rating of circuit breaker needed for 300 KVA load in 33 KV supply line in a transformer of 33 KV / 415 Volt ?
What will happen to the protection and metering, if the polarity of a single or two PT/PTs in three phase system is reversed? Please provide reference if any.
What is time response of the control system?
What is DC series motor?
Terminal blocks is used for segregate the connections... There is any principle for terminal block..?
Discuss about gear cutting machines.
what is v/f control in VFD?
What is the permissible limit of shaft voltage for 6.6 KV motors ? Why? Is there any standard is available?
What is the function of probe in cro?
kindly send me 11KV MV motor differential protection procedure by primary injection method.
WHAT IS MOBILE SUB-STATION? & REALLY BENEFIT IN INDIA
sir,in our plant we r using SATEC PM172E power reading meeters in HT panel side it is monitoring the MB data smart viewer(sever).but last one week we did not get readings inthe server only available in meeter.tell me how communicate meter and server. and also what steps we take for checking.
if we have a industrial load of 400 kilowatts with 415 volt AC then how much total harmonic distortion (thd%) should be acceptable for steady power system.